Nexus 5K interfejs vfc jest w initializing

#1

#1 Post autor: martino76 »

Witam,

Konfiguruje FCoE i natknąłem się na pewien problem a mianowicie interfejs vfc jest up ale VSAN jest w procesie initializing

Kod: Zaznacz cały

IEDP03-N5K-SW02# sh int vfc 154
vfc154 is trunking
    Bound interface is port-channel154
    Hardware is Ethernet
    Port WWN is 20:9a:8c:60:4f:98:10:bf
    Admin port mode is F, trunk mode is on
    snmp link state traps are enabled
    Port mode is TF
    Port vsan is 411
    Trunk vsans (admin allowed and active) (411)
    Trunk vsans (up)                       ()
    Trunk vsans (isolated)                 ()
    Trunk vsans (initializing)             (411)
    1 minute input rate 0 bits/sec, 0 bytes/sec, 0 frames/sec
    1 minute output rate 0 bits/sec, 0 bytes/sec, 0 frames/sec
      0 frames input, 0 bytes
        0 discards, 0 errors
      0 frames output, 0 bytes
        0 discards, 0 errors
    last clearing of "show interface" counters Mon Feb 12 07:38:26 2001

    Interface last changed at Mon Feb 12 07:38:35 2001

Kiedy sprawdzam interfejs vfc to widzę ze oczekuje na flogi, zastanawiam się czy problem nie jest po stronie serwera i z jakiegoś powodu nie wysyła mi FLOGI. Rozmawiałem z adminem i twierdza, ze po ich stronie wszystko jest ok.

Kod: Zaznacz cały

IEDP03-N5K-SW02# sh int vfc 154 trunk vsan 411
vfc154 is trunking
    Vsan 411 is down (waiting for flogi)
QOS policy mam takie jak powinno być sprawdzałem na obu switchach i na drugim dla takiej samej konfiguracji interfejs vfc jest up

Kod: Zaznacz cały

IEDP03-N5K-SW01# sh int vfc 154
vfc154 is trunking
    Bound interface is port-channel154
    Hardware is Ethernet
    Port WWN is 20:99:8c:60:4f:86:9d:ff
    Admin port mode is F, trunk mode is on
    snmp link state traps are enabled
    Port mode is TF
    Port vsan is 410
    Trunk vsans (admin allowed and active) (410)
    Trunk vsans (up)                       (410)
    Trunk vsans (isolated)                 ()
    Trunk vsans (initializing)             ()
    1 minute input rate 64 bits/sec, 8 bytes/sec, 0 frames/sec
    1 minute output rate 80 bits/sec, 10 bytes/sec, 0 frames/sec
      825 frames input, 87932 bytes
        0 discards, 0 errors
      826 frames output, 111724 bytes
        0 discards, 0 errors
    last clearing of "show interface" counters Fri Feb  9 22:24:20 2001

    Interface last changed at Fri Feb  9 22:29:50 2001

Config

Kod: Zaznacz cały

interface vfc154
  bind interface port-channel154
  switchport trunk allowed vsan 411
  no shutdown

policy-map type network-qos JUMBO_MTU
  class type network-qos class-fcoe
    pause no-drop
    mtu 2158
  class type network-qos class-default
    mtu 9216
system qos
  service-policy type network-qos JUMBO_MTU
  service-policy type queuing input fcoe-default-in-policy
  service-policy type queuing output fcoe-default-out-policy
  service-policy type qos input fcoe-default-in-policy

vsan database
  vsan 411 interface vfc154

vlan 411
  fcoe vsan 411


Mial ktoś podobny problem bo w sumie nie wiem co jeszcze mogę sprawdzić, config wygląda w por zadku i raczej niczego nie przegapiłem?

Pozdro,

martino76
CCIE
CCIE
Posty: 883
Rejestracja: 17 gru 2010, 15:23
Lokalizacja: Barczewo

#2

#2 Post autor: martino76 »

Temat do zamknięcia problem był po stronie HP Blade.